4-20 mA Unit with wemos S2 mini ESP32
-
@robski thanks for the answer
so you mean if I measure with multimter 4.0 mA (which is true for the sensor) and the unit shows me 7.2 mA I should set the calibrated value to 4.0 ?
Because this is not mentioned anywhere in a readme file or manual or in the description of the device, and it is not made in the example file at github
but I am a beginner.... -
@obstbauer thats what i did with mine initially, calibrate with known current value
-
-
@obstbauer yeah thats the registers table, I used Uiflow2 with calibration block but you are using not M5Stack controller I see
-
@robski what value do you take for "index" in the function
void MODULE_4_20MA::setCalCurrent(uint8_t index, uint16_t value)
-
@obstbauer haven't used index value
in uiflow2 ..ain4_20ma_0.set_cal_current(10) to set 10mA
ain4_20ma_0.set_cal_current(20) to set 20mA -
@robski yes maybe in uiflow2 but the function for the c program asks for an index and a value
-
I see really strange behaviour and I don't know the reason and I get no answers from the support.....
The example code from M5Stack say that the currentvalue should be divided by 100:canvas.printf("Current:%.2fmA", (float)(meter.getCurrentValue(0)) / 100.0);
The values I get I have to divide by 10 to get the right current in mA.... and the other issue is that I can only use half of the measurement range, at 12.5 mA the ADC sends 65520...
maybe someone has an idea ?
-
change to a raspberry PI4 seems to be no solution too.....
it woud be nice if there would be a better documentation for people who want to use the units outside the m5stack universum.... -
@obstbauer this is uiflow example with raw value and float too